hi all,
after testing i found an minor issue with my breakout-box. everything is working as intended but i get annoying double triggers on some modules. when i connect the same modules to my robokop sequencer or other trigger source everything is fine. could it be a grounding issue?
the +/-12V for the AOUT NG is coming from my eurorack and the +5V for AOUT NG and the LineDriver Receiver from an additional psu. the external psu (5v) is in the middle of the ribbon cable between AOUT NG and the receiver as suggested by latigid on. i also enabled the 1ms trigger but it makes no difference.
when using the same trigger on another module it works so i guess i can rule out the double trigger is coming from the sequencer itself.
please help
rbv2
Edited by rbv2
Hola,
just tested the new dedicated midiphy eurorack modules, that are in the works - while i don't have a big modular setup, i measured and tested gate and trigger outs and had no issues (tested triggering the "Freeze" and the "Trig" functions on a MI Clouds and also measured signal outputs with a scope). Therefore, I would also expect maybe a common ground problem on your side? Have you grounded the external PSU and the LineDriver Receiver to the modular/rack common ground?
The new euroceiver module (left in the pic below, which still uses handmade paper/epoxy panels for fit-testing) has a built-in voltage regulator, that allows generating the required 5v from the +12V modular rail, which will spare you the external psu and would not require you to send the +5v down the DB25 cable from the SEQ, which might be problematic.
large.60747229_449092429199798_104122892
Many greets and have a nice weekend!
Peter
hi peter,
thanks a lot for you answer.
8 hours ago, Hawkeye said:
Hola,
at the moment i have wired 12V+/- and GND directly from a doepfer bus board to J3 of the AOUT NG the external psu is in the middle of the cable from JAOUT of the receiver to J1 of the AOUT NG. (Vs & Vd) . by common ground do you mean i should connect the Vs line of 5V PSU to the GND of J3 at the AOUT NG? all the jacks (gate, trigger, cv) are connected to ground and since the panel is made of aluminium the gnd of both psu's is connected.
unfortunately i saw the information about the new modules too late. i would rather use them but i had already bought all the parts and ordered a panel at schaeffer..:doubt:
i have also learned that the 5v on the doepfer boards are not there at all although it is written on it :rolleyes:
thanks!
Probably @latigid on can help you out way more than i can... but i just looked up the AOUT_NG schem and it seems analog ground can be tied to digital ground (see middle of the schem), maybe by a jumper? If that is the case, i think the grounds should be all tied down together and nothing is floating, which might cause problems. We are using the AOUT (not NG) module, so i don't really know much about the NG.
Two more questions: do you use a DOUT module for the triggers? I think, if an analog out would be used for that digital purpose, the DAC might "overshoot" or ring or might not be quick enough, but that is wild speculation. Do you have access to a scope, so you can see the trigger output waveform?
Peter
hi peter,
at the shematic i can see the point you refering to but there is no jumper or place for a pinheader.
yes i use the DOUT module for 8x Gate, 16x Trigger an 8x Clock the AOUT NG is for CV only.
a friend of mine will lend me his scope. but i don't have one right now.
thank you!
Edited by rbv2
On 5/23/2019 at 6:22 PM, rbv2 said:
hi all,
please help
rbv2
I repeat my advice from the other thread:
Could it be the HW config settings or an issue with midi loops feeding back in? More than one track assigned to AOUT?
The perennial IDC cabling issue would also be worth checking.
You could also test with _NG again and in MIOS terminal
set dout x 1
to check if the problem is replicated. For x you have to count the number of shift register outputss in the chain, starting from 0-7 for the first one. Or simply replace x with 'all'.
Check the resistance of your 0V from the Eurorack to somewhere on the SEQ e.g. pin 2 on a MIDI out (the one at 6 o'clock).
In the line receiver, is jumper J3 closed? This could cause interference on the +5V line if there are two PSUs fighting.
If you use an external PSU you must connect the 0V together with the +/-12V PSU 0V common line. A metal panel is not a good (and some would say unsafe) method of achieving common 0V.
I guess you are not using the +5V on the bussboard? But if you are, maybe you don't have +5V connected and the modules are being parasitically powered from the digital signals? (This is not good for CMOS btw.) Did you measure correct +5V on the modules?
There is only one "ground" and the separation of analogue/digital 0V is a complex and often misunderstood topic. On AOUT_NG the two are connected underneath the DAC chip; there is no jumper etc.
A scope might be useful to see what's going on.
hi latigid on,
thanks a lot for your answer.
- since i have made no changes in the HW Config beside setting the 1ms-option and SRs for clocks, gates & Trigger i would assume no
- all tracks muted except for the one sending triggers to CH16
- checked all cables visually again
- the resistance between 0V Eurorack and pin 2 of a Midi Socket oscillates between 1,8-2,5 Ohm
- no jumper in J3
- the double trigger only occours on some modules and depends on the setting of the length in the parameter layer, when length is 4% it's almost gone, it's acting like a gate..
- I'll try to do the tests in mios when I understand how it works
so the connection underneath the DAC is not sufficient then?
yes, i am using an external power plug. i get 4,96V on J2 of AOUT NG and 4,96V on J19 of the Receiver
unfortunately I still have to wait for the scope..
thanks
rbv2
Edited by rbv2
Everything sounds correct.
Yes and no? Try to have the 0V common to both PSUs, i.e. at the source of the power.
@latigid on
thanks!
to be on the safe side, I made a drawing.
it shows my current wiring. the black line with the question mark shows how I understand it.
would that be okay?
thank you!
rbv2
cgnd.thumb.jpg.d62231f910256079c225d6bda
Edited by rbv2
Is the external PSU actually +5/-5V? So a 10V supply?
The 0V should be common rather than 0V to -12V. I think that's what your diagram shows, but the 0V of the PSU should connect to the yellowish wire on your diagram, not the black -12V
no, its 5V didn't know how write it correctly. :blush:
yes, isn't so well drawn but that's what I meant.
thanks. i try it and report
thanks a lot, it's working much better now also the random triggers when inserting cables are gone now :)
only get double triggers on very long "lenght" settings wich i assume is normal behavior. are those real triggers or very short gates?
thanks @Hawkeye and @latigid on for your support and patience
you deserve a beer :cheers:
btw. where is the "buy hawkeye a beer" button?
Edited by rbv2
2 hours ago, latigid on said:
I'm not 100% sure what you mean with very long lengths. Does it remain when the gate length is set to glide? Video?
when sending out triggers from AOUT Ch16 and then select in the parameter layer "lenght" i can change the lenght of the trigger/gate from 1% to Glide
at 1% - no trigger
at 2% - sporadic trigger
from - 3-20% steady trigger
from - 21-100 % double trigger with increasing distance (21% narrow / 100% wide)
glide - only the first trigger
before we fixed the grounding issue i got double triggers starting at 5% and other problems but now i'm pretty shure those are gates and not triggers making some modules being triggered at the beginning and the end of that rectangular pulse.